What is the recommended amount of CFM's for a ventilation system regarding the fan?
Dale M.
2010-04-13, 12:42pm
The recommended values are 125 cfm for every square foot of "face opening" for a open hood...
If you are using a fume "cabinet" (hood+sides) I believe you can get by with 100cfm per sq-ft of face opening...
The "face opening" is height x width for a cabinet or width x depth for simple hood...
As a example on a 24 x 30 inch fume hood....
24 x 30 = 720 square inches
720 sq-in / 144 = 5 sq-ft
5 sq-ft x 100cfm = 500cfm
but if its a open hood its:
5 sq-ft x 125 = 625 cfm
Funnel systems are a bit different, the exact values have not been really defined as exact as a hood, but a 6-7 inch duct system with about a 8-10 inch square (or round) funnel seems to need about 350-400 cfm (minimal) to function effectively...
Dale