View Full Interactive Version Of This Page : CFM?


abeadgal
2006-11-26, 6:09pm
I have been reading a lot on ventilation and I'm afraid this might be a question without an easy answer but.........
What is the minimum CFM for adequate ventilation for a small one car garage/studio? Is there some formula or is it just a standard amount?
Thanks,
Kristi

MikeAurelius
2006-11-26, 7:06pm
It is base on the "face" or opening of the hood you are going to use. For overhead hoods (similar to a kitchen hood), use 125 CFM per square foot of hood opening. For enclosed workstation hoods, use 100 CFM per square foot of "face" or opening.

abeadgal
2006-11-26, 7:31pm
oh, this gets more and more confusing for me...so, is a kitchen type hood vent adequate if it is mounted just above the work area?
Thanks so much for you help!!
Kristi

MikeAurelius
2006-11-27, 5:09am
Yes, but be sure to allow for adequate clearance so you don't bang your head every time you stand up or sit down. Typically a minimum of 30" to a maximum of 42" above the table should be fine.

abeadgal
2006-11-27, 9:37am
Thanks for the info. I really appreciate it! I needed it as simple as possible. :)
Thanks,
Kristi