Quote:
Originally Posted by MikeAurelius
If you have a HotHead torch -- DO NOT RUN THE FUEL LINE THROUGH THE WALL.
It is illegal to run more than 20 PSI of fuel gas through any wall structure.
That said, if you are using a dual gas torch (oxygen/propane), you will need to have two valves, one for each side of the wall (it seems like overkill, but it is code). On the inside connection after the valve, simply use a brass barbed connector for 1/4" rubber hose, and match the threaded side to whatever size pipe you are using.
On the outside, do exactly the same.
|
Actually it is illegal to run NG through wall at more than 5psi... Propane limit is 20psi
If using a propane tank, the tank valve IS the "outside" shutoff valve. If using NG yes you need a second valve in plumbing outside wall at "entry". This is something gas company would install "before" meter.
Dale
__________________
You can lead a person to knowledge, but you can't make them think.