Default Ventilation condensation

I am in the process of moving my studio into our former garage. The plan was to take the ventilation through the attic and out. Today my husband expressed concern that this would create condensation and put moisture into the blown-in insulation. The room will be kept around 60F and the attic is the same as the outdoors. During the winter that can be anywhere from -05F to 35F. Has anyone had this happen? Any thoughts would be appreciated.

Thanks, PegC
Reply With Quote
  #2  
Old 2011-01-27, 9:04pm
cheng076's Avatar
cheng076 cheng076 is offline
Curmudgeon Engineering
 
Join Date: Feb 15, 2006
Location: Near Seattle, WA
Posts: 1,723
Default

Since the vent ducts will contain air warmer than the attic air there will be no condensation into the attic insulation. There may be some inside the ducts as you then have warm air with moisture from combustion and a cool outside the duct temp. Condensation occurs when warm moist air is cooled. The warm air flowing so fast thru the duct should evaporate the moisture. JMHO
PJ
Reply With Quote
  #3  
Old 2011-01-28, 8:31am
meg10yr's Avatar
meg10yr meg10yr is offline
Member
 
Join Date: Oct 28, 2007
Location: Batavia, NY
Posts: 37
Default

Thanks PJ.
Reply With Quote
  #4  
Old 2011-01-28, 8:41am
RSimmons's Avatar
RSimmons RSimmons is offline
Senior Member
 
Join Date: Aug 01, 2005
Posts: 2,159
Default

One question to clarify: You intend to exhaust through a duct that goes through the roof and to the outside and you are concerned about condensation on the outside of the duct dripping into the insulation, not exhausting into the attic space so that the material is carried away by your normal attic ventilation. Correct?

Robert
__________________
Robert Simmons
(Former) Director for Bead Donations
Beads of Courage, Inc.
Reply With Quote
  #5  
Old 2011-01-28, 9:21am
meg10yr's Avatar
meg10yr meg10yr is offline
Member
 
Join Date: Oct 28, 2007
Location: Batavia, NY
Posts: 37
Default

Robert, that is correct. The duct will have 1 90deg bend and travel 25' to the exsisting gable vent fan.

PegC
Reply With Quote
  #6  
Old 2011-01-28, 9:59am
laserglass's Avatar
laserglass laserglass is offline
old fart
 
Join Date: Apr 18, 2006
Location: st paul mn
Posts: 778
Default

Quote:
Originally Posted by meg10yr View Post
Robert, that is correct. The duct will have 1 90deg bend and travel 25' to the exsisting gable vent fan.

PegC
you need a much much shorter, direct path to the outside and a squirrel cage fan for that duct only. and you also need another short direct path to the outside for make up air that is not located near where your ventilation duct vents or where your outside propane tanks are located. you cannot just vent your ventilation duct near where your attic ventilation fan is located.
__________________
Mark Wilson

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

Last edited by laserglass; 2011-01-28 at 10:01am.
Reply With Quote
  #7  
Old 2011-01-28, 10:51am
meg10yr's Avatar
meg10yr meg10yr is offline
Member
 
Join Date: Oct 28, 2007
Location: Batavia, NY
Posts: 37
Default

I have a natural gas hookup. There is 640 CFM in the hood as well as the attic fan at the end of the run. I plan to put baffles on the hood similar to a barley box. I will do a smoke test at various stages of installation. if there is still a need for it I will box in the attic fan and attach the ducting to the box. There are two double hung windows on the wall next to me and a man door and overhead door that can both be open as necessary. All make up air sources are well away from the vent fan.

Thanks for the input!
Reply With Quote
  #8  
Old 2011-01-28, 11:20am
cheng076's Avatar
cheng076 cheng076 is offline
Curmudgeon Engineering
 
Join Date: Feb 15, 2006
Location: Near Seattle, WA
Posts: 1,723
Default

Sorry to jack the thread but....
Hey Mark, where you been? Haven't seen you post in some time.
Reply With Quote
  #9  
Old 2011-01-28, 11:23am
RSimmons's Avatar
RSimmons RSimmons is offline
Senior Member
 
Join Date: Aug 01, 2005
Posts: 2,159
Default

I'm pretty sure that a 640 CFM fan is going to be seriously underpowered for your length of duct as the static pressure is going to be too high for effective ventilation. An extra fan at the end will just complicate matters. You'll be better served to get a much bigger squirrel cage blower, build it into a vacuum plenum and run your exhaust through that directly to the outdoors.

Robert
__________________
Robert Simmons
(Former) Director for Bead Donations
Beads of Courage, Inc.
Reply With Quote
  #10  
Old 2011-01-28, 1:36pm
laserglass's Avatar
laserglass laserglass is offline
old fart
 
Join Date: Apr 18, 2006
Location: st paul mn
Posts: 778
Default

Quote:
Originally Posted by cheng076 View Post
Sorry to jack the thread but....
Hey Mark, where you been? Haven't seen you post in some time.
i don't post much any more. i got tired of arguing with people who were ignorant of facts.
__________________
Mark Wilson

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #11  
Old 2011-01-28, 2:19pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Quote:
Originally Posted by RSimmons View Post
I'm pretty sure that a 640 CFM fan is going to be seriously underpowered for your length of duct as the static pressure is going to be too high for effective ventilation. An extra fan at the end will just complicate matters. You'll be better served to get a much bigger squirrel cage blower, build it into a vacuum plenum and run your exhaust through that directly to the outdoors.

Robert
I agree with this thought completely...

you are building a patch work system that will cause more grief than pleasure...

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #12  
Old 2011-01-28, 2:20pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Quote:
Originally Posted by laserglass View Post
i don't post much any more. i got tired of arguing with people who were ignorant of facts.
I hear that....

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #13  
Old 2011-01-28, 6:13pm
meg10yr's Avatar
meg10yr meg10yr is offline
Member
 
Join Date: Oct 28, 2007
Location: Batavia, NY
Posts: 37
Default

??????????

Thanks guys!
Reply With Quote
  #14  
Old 2011-01-28, 6:32pm
RSimmons's Avatar
RSimmons RSimmons is offline
Senior Member
 
Join Date: Aug 01, 2005
Posts: 2,159
Default

Quote:
Originally Posted by meg10yr View Post
??????????
Safety in general and ventilation in particular are things that some people simply choose to ignore for a host of reasons. I'm glad that you are taking it seriously and have sought advice here before you spent time and money on your setup.

Robert
__________________
Robert Simmons
(Former) Director for Bead Donations
Beads of Courage, Inc.
Reply With Quote
  #15  
Old 2011-01-28, 7:09pm
meg10yr's Avatar
meg10yr meg10yr is offline
Member
 
Join Date: Oct 28, 2007
Location: Batavia, NY
Posts: 37
Default

Thank you Robert. This has been my husband's project and he will do it his way. He has agreed that if I can show him it is inadequate we can do it the way I suggested - with a squirrel cage fan at the 90deg angle. For the past couple of years I have been in an uninsulated 5x7 shed with a direct vent for the hood through the roof. It is going to be great to have this new, comfortable environment to work in but I will do everything I can to ensure it is also safe.

PegC
Reply With Quote
  #16  
Old 2011-01-28, 10:25pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Through all this 25 feet of duct and fans and whatnot I have yet to see any calculations... What is hood (fume cabinet) opening size... What is duct diameter.... Has duct velocity been calculated, has static pressure been calculated....

IT may be your husbands project, but there is whole set of calculation that are proven to work, and if you follow then you almost have fool proof system... There is even a spread sheet available to use to help you....

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal

Last edited by Dale M.; 2011-01-29 at 9:30am.
Reply With Quote
  #17  
Old 2011-01-29, 9:23am
laserglass's Avatar
laserglass laserglass is offline
old fart
 
Join Date: Apr 18, 2006
Location: st paul mn
Posts: 778
Default

if you have a fan that can move 650 CFM through a duct that is 3 feet long, that same fan will move 65 CFM through a duct that is 10 times as long or 30 feet. and that is neglecting things like duct roughness, static loss due to elbows in the duct. you need to cut a hole in your home, that is the reality. i would suggest a sidewall rather than the roof, so you don't have to deal with rain/snow. alternatively, construct a baffle to pass your vent duct out through an existing window. but you cannot also use the window for make up air.
__________________
Mark Wilson

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

Last edited by laserglass; 2011-01-31 at 12:02pm.
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump




All times are GMT -7. The time now is 3:17am.


Powered by vBulletin® Version 3.7.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Your IP: 18.218.38.125