Simple ventilation...is it possible?
I am hoping that this hood range will work. If so, it would just make my life so much easier and get my studio done so much faster. http://www.tomorrowskitchen.com/FW-3503.html or http://www.tomorrowskitchen.com/KB-36.html.
Thanks for your input
Joyce
__________________
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 10:41am
|
 |
silver glass addict
|
|
Join Date: Oct 05, 2006
Location: San Francisco
Posts: 13,002
|
|
Joyce,
Nice hoods! I think either one will work. Here are the calculations based on the hood sizes:
KB36 @ 860 CFM
35.4 x 19.7 = 697.38 / 144 = 4.84 x 125 = 605 CFM
FW3503 @ 870 CFM
47.4 x 19.7 = 933.78 / 144 = 6.49 x 125 = 811 CFM
The only concern is that since both of them are wall mount hoods . . . at 19.7" depth, you may be too close to the back wall. At a minimum, you should line the back wall like a back splash, perhaps with a piece of sheet metal?
Hope this helps!
__________________
Hayley
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts. | To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 10:43am
|
 |
Senior Member
|
|
Join Date: Nov 16, 2005
Posts: 178
|
|
Thanks Hayley. I might actually get to move my studio inside off the back patio.
Joyce
__________________
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 10:45am
|
 |
silver glass addict
|
|
Join Date: Oct 05, 2006
Location: San Francisco
Posts: 13,002
|
|
Joyce - I just edited my post to add my concern. . . realized the depth of the hood may post an issue.
__________________
Hayley
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts. | To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 12:00pm
|
Member
|
|
Join Date: May 12, 2007
Posts: 54
|
|
I had my carpenter install two hoods back to back into one exhust. I waited far too long to do some sort of ventalation. Now I am all set-I love it and it was"simple". Good luck.
Mimi
|

2008-05-20, 4:43pm
|
 |
Salt Box Beads
|
|
Join Date: Oct 23, 2005
Location: Heading to Paradise
Posts: 4,166
|
|
I didn't check your links but isn't there something about being sure to get exhausting hoods and not recirculating? or something like that?
Lorraine
|

2008-05-20, 7:20pm
|
 |
Senior Member
|
|
Join Date: Nov 16, 2005
Posts: 178
|
|
Mimi- Does this mean you doubled the depth? That is an interesting idea.
Lorraine_ I plan to vent out the roof. Thanks.
__________________
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 7:21pm
|
 |
Gentleman of Leisure
|
|
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
|
|
If you go to the links and download the "Installation Instructions" you wil find they are direct vent to outside.....
Only thing I can see to these hoods as a negative is the "grease trap/filters" but then they can be easily removed to increase effectiveness....
Several times these particular hoods have come up as a ventilation solution and if installed properly seem like a very viable solution. But this is just going by the manufacturers specifications.
Dale
__________________
You can lead a person to knowledge, but you can't make them think. To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
|

2008-05-20, 7:24pm
|
 |
Senior Member
|
|
Join Date: Nov 16, 2005
Posts: 178
|
|
Dale,
Do you think the depth is a problem? I can see that it could get pretty hot. I am on a Mini CC. I plan on putting up a sheet of stainless steel behind the torch with space betweent he metal and the wall. Thanks.
Joyce
__________________
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|

2008-05-20, 8:30pm
|
 |
Gentleman of Leisure
|
|
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
|
|
I don't think depth of hood will be a problem...
For safety it never hurts to have non flammable back board with a airspace behind it, as long as airspace is not sealed, it should be open to convection cooling...
Dale
__________________
You can lead a person to knowledge, but you can't make them think. To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
|

2008-05-20, 9:03pm
|
 |
Senior Member
|
|
Join Date: Nov 16, 2005
Posts: 178
|
|
Dale, thanks a lot. Thanks to you and Hayley I think moving into my studio is a real possibility now. Thank you thank you.
Joyce
__________________
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
|